Postby Chilton82 » Sat May 30, 2015 2:38 pm

If the smallest fuse that I have is a 5 amp but the load on the circuit is going to be much smaller (sub 1 amp) on a 16 gauge wire will the 5 amp fuse be alright? Obviously it'll be overkill or should I go out and pick up a 1 amp fuse?
Chilton82
Teardrop Inspector
 
Posts: 7
Joined: Mon May 04, 2015 3:23 pm

Re: Fuse Question

Postby H.A. » Sat May 30, 2015 2:50 pm

5a will be ok. It definitely protects a 16awg conductor.
Depending on your how robust the appliance, you might want to go lower or place a fuse on the appliance its self.
H.A.
The 300 Club
 
Posts: 461
Images: 0
Joined: Tue Nov 15, 2011 8:16 pm

Re: Fuse Question

Postby Chilton82 » Sat May 30, 2015 3:21 pm

H.A. wrote:5a will be ok. It definitely protects a 16awg conductor.
Depending on your how robust the appliance, you might want to go lower or place a fuse on the appliance its self.


They're just led lights.