Postby Dalorin » Wed Aug 12, 2015 10:26 am

All,

The PD4045 has two branch ratings, black wires are for 20 amp max and red for 30. Should I use fuses of those sizes or should I under size them to be safe?

Thanks in advance
Dalorin
Teardrop Master
 
Posts: 135
Joined: Wed Dec 31, 2014 4:50 am

Re: PD4045 branch fuses

Postby noseoil » Wed Aug 12, 2015 10:44 am

Fuses (breakers) are there to protect the wiring, not the device or appliance attached to the wire. Your wire size should always withstand the load attached to it, & the fuse should always go before the wire is hot.
Build log: viewtopic.php?f=50&t=60248
The time you spend planning is more important than the time you spend building.........

137905
User avatar
noseoil
1000 Club
1000 Club
 
Posts: 1820
Images: 669
Joined: Sun Apr 27, 2014 8:46 am
Location: Raton, New Mexico, living the good life!

Re: PD4045 branch fuses

Postby Dalorin » Wed Aug 12, 2015 11:01 am

@noseoil, I concede that ordinarily that may be the case when run just from a battery, however, in this situation the charge controller could be delivering the load. So it's protecting power system circuitry as well.

I'm using 12awg stranded speaker wire throughout. So I'm pretty confident it will handle a 30 amp load across a max 20 ft length of wire.
Dalorin
Teardrop Master
 
Posts: 135
Joined: Wed Dec 31, 2014 4:50 am
Top

Re: PD4045 branch fuses

Postby MtnDon » Wed Aug 12, 2015 11:52 am

12 AWG wire is usually limited to 20 amps

http://www.cerrowire.com/ampacity-charts
Our 6x12 deep vee nose cargo trailer camper conversion... viewtopic.php?f=42&t=58336

We have a small off grid cabin we built ourselves in the NM mountains; small PV solar system; 624 watts PV, Outback CC & inverter/charger ... http://countryplans.com/smf/index.php?topic=2335.0
User avatar
MtnDon
2000 Club
2000 Club
 
Posts: 2200
Images: 24
Joined: Sun Aug 19, 2012 10:57 pm
Location: New Mexico
Top

Re: PD4045 branch fuses

Postby Dalorin » Wed Aug 12, 2015 1:07 pm

Fair enough. 20 amp. I'll just run the 30 amp lines to sockets in the galley on 10awg. That's only a couple feet anyhow.

My question on the fuse ratings still stands. I guess I'll call progressive dynamics.
Dalorin
Teardrop Master
 
Posts: 135
Joined: Wed Dec 31, 2014 4:50 am
Top

Re: PD4045 branch fuses

Postby Dalorin » Wed Aug 12, 2015 1:38 pm

I just got off the phone with progressive dynamics. They said that you can use up to 30amp fuses on the 30 amp lines and up to 20 on the 20 amp lines. However, they did suggest sizing it for the load.

I have a fan vent that should not draw more than 2 amps. I'm likely to put a smaller fuse on the vent. Also likely to use smaller fuses for my lights.
Dalorin
Teardrop Master
 
Posts: 135
Joined: Wed Dec 31, 2014 4:50 am
Top

Re: PD4045 branch fuses

Postby noseoil » Thu Aug 13, 2015 7:24 am

Here's a chart which may be useful. Most of my loads will just use 5 amp fuses, since LED lighting draws such a small amount of current. The biggest load I have is really just the chargers at the headboard for phones, about 2 amps X 2 outlets or total possible load of 4 amps at 14', if both phones need a charge at the same time. 18 gauge wire is plenty for LED's & relatively small loads.

The high power load runs off of a 110v inverter & feeds the galley outlet on wiring which is stranded 14 gauge house type wire. The entertainment system also runs from the inverter. The PD4045 supplies shore power for the front-mounted AC & another galley outlet at the counter. I'm not going to bother to try to power the AC with the battery, as it doesn't have enough capacity to run for long enough with the load the AC creates to do any good.

Image
Build log: viewtopic.php?f=50&t=60248
The time you spend planning is more important than the time you spend building.........

137905
User avatar
noseoil
1000 Club
1000 Club
 
Posts: 1820
Images: 669
Joined: Sun Apr 27, 2014 8:46 am
Location: Raton, New Mexico, living the good life!
Top

Re: PD4045 branch fuses

Postby Dalorin » Thu Aug 13, 2015 9:05 am

@noseoil Thanks! That is helpful.
Dalorin
Teardrop Master
 
Posts: 135
Joined: Wed Dec 31, 2014 4:50 am
Top

Re: PD4045 branch fuses

Postby Shadow Catcher » Thu Aug 13, 2015 4:49 pm

Yes the wiring into the PD is 20A what you attach to that may not be. 14 ga was used in our tear and while you are protecting the wiring why not protect what is attached to it as much as practicable.