So, exactly how mutch propane can be expected to seep out of the hose? If it was a great amount you would be able to smell it.
None..... It only happens if there is a structural defect of inner wall of hose....
Dale
Dale, From my experience, MANY is more accurate. We hydro static test each and every LPG assembly we build, not so much to see if it leaks, we already know most will leak some propane, that's why the cover is pin pricked.
We hydro static pressure test to see if the hose, and mostly our fitting installation will withstand 2 times the working pressure, so we can supply test documentation. We mark the crimped fitting location, and check for any movement during the test. If an end blows off, that's a lot more serious than a tiny leak through the cover.
We experience approx. a 5% failure rate during hydro static pressure testing where water squirts from a bunch of holes like a law sprinkler! Not everybody tests their LPG assemblies. Most Non DOT hoses are probably not tested!
What everyone needs to understand is LPG flexible hose connections are designed for well ventilated areas where tiny propane leaks are not normally an issue. It's when this hose is used indoors or other confined area where the buildup of gas can be a problem. Indoor use requires hard plumbing, not hose!!
DH, To answer your question: I would assume any rubber (non barrier) hose will "probably" leak some propane, is this a problem? Probably not, UNLESS YOU KEEP THE PROPANE FILLED HOSE IN A CONFINED AREA.
There are probably hoses such as Teflon with SS overbraid or convoluted SS with SS overbraid that would be fine in confined ares, but may be cost prohibitive, and not meet DOT requirements.
The bottom line... Be safe, be safe, be safe... and consult your State and the Federal DOT for specific requirements concerning Propane connections and transported on public highways. Use hard plumbing, either black iron, copper tubing or what ever meets the requirements, and use the flexible (hose) connection only to connect to the appliance using appropriate methods, especially keeping the hose in ONLY well ventilated areas.
Safety Please......