Anything electric, AC or DC

Wire between Batteries and PD4045

Postby RetchedOne » Thu May 21, 2015 1:03 pm

What gauge of wire should I run between the PD4045 and the batteries (2 6 volt Costco batteries)?
The run will only be about 5 feet
No inverter, just led lights, 12v outlets for phone. NT-16seq furnace
There will be a disconnect and fuse/breaker on the positive batter cable before the PD4045.

6 gauge?
RetchedOne
Teardrop Advisor
 
Posts: 98
Images: 9
Joined: Sat Nov 29, 2014 12:09 pm
Location: Marysville, WA

Re: Wire between Batteries and PD4045

Postby H.A. » Thu May 21, 2015 1:34 pm

Temperature, insultion type and other factors play in to it,
But basically worst case, 6awg woll carry around 55 amps.
What is a huge amount of DC power within most any RV.
H.A.
The 300 Club
 
Posts: 461
Images: 0
Joined: Tue Nov 15, 2011 8:16 pm

Re: Wire between Batteries and PD4045

Postby lrrowe » Thu May 21, 2015 2:59 pm

I contacted the manufacturer several months ago with a similar question. They told me that 4 GA is the largest size to use for my unit which is what I ordered for this cable. As far as the smallest you can get away with, hopefully others can join in and advise.
Bob

First Post on Purchase of Trailer: http://www.tnttt.com/viewtopic.php?f=42&t=60722
Hot water infloor and radiator heating project:[url]http://www.tnttt.com/posting.php?mode=reply&f=54&t=62327[/

Image Image
User avatar
lrrowe
Donating Member
 
Posts: 3285
Images: 439
Joined: Sun Feb 10, 2013 5:54 am
Location: SW Virigina
Top

Re: Wire between Batteries and PD4045

Postby RetchedOne » Thu May 21, 2015 3:01 pm

lrrowe wrote:I contacted the manufacturer several months ago with a similar question. They told me that 4 GA is the largest size to use for my unit which is what I ordered for this cable. As far as the smallest you can get away with, hopefully others can join in and advise.



I'll go with 4 GA as well then.

Thanks!
RetchedOne
Teardrop Advisor
 
Posts: 98
Images: 9
Joined: Sat Nov 29, 2014 12:09 pm
Location: Marysville, WA
Top

Re: Wire between Batteries and PD4045

Postby lrrowe » Thu May 21, 2015 3:19 pm

I ordered custom made ones from http://www.genuinedealz.com/custom-cables. They appear to be well made and reasonably priced. Far better then I could do with the limited tools I had.

See http://tnttt.com/viewtopic.php?f=30&t=6 ... nuinedealz for photos of the cables.
Bob

First Post on Purchase of Trailer: http://www.tnttt.com/viewtopic.php?f=42&t=60722
Hot water infloor and radiator heating project:[url]http://www.tnttt.com/posting.php?mode=reply&f=54&t=62327[/

Image Image
User avatar
lrrowe
Donating Member
 
Posts: 3285
Images: 439
Joined: Sun Feb 10, 2013 5:54 am
Location: SW Virigina
Top


Return to Electrical Secrets

Who is online

Users browsing this forum: No registered users and 1 guest