I unplugged from the generator and plugged it into utility power, and the same thing happened. WTF? I unplugged the charge controller and plugged it back in and boom, 46 amps. The charger maintained 46 amps till the battery was charged. You can see where I unplugged-plugged the controller as the current jumps up to 46 amps This is the entire charge cycle:
Interestingly, the voltage jumped up from 13.5 to around 13.8V with the current bump, which is in the recommenced range for LiFePO4 charging. I like how the charger changes mode at about 14V and tapers the current down to nothing until the battery is at 100% charged. Here's a close up of the charger finishing up:
I used a Kill a Watt to measure some AC electrical parameters while the charger was full output:
Drawing 8.8 amps at 120V:
796 watts output the generator with 634 amps going into the battery. That's about 80% efficiency while charging at full output:
Power factor is awful, as low as 0.6 when the charger was at 20 amps, rising to 0.7 when loaded:
The real surprise was the Volt-Amp load; I wouldn't have guessed the generator would carry this since the power factor is so low. A 0.8 power factor is what most commercial generators are rated at:
So here's some conclusions I've drawn from this test.
-I'll keep my 1000w generator, I was considering trading up to a 2000 but I don't need one yet. The generator won't run the A/C so if I do upgrade it will be to run that.
-The generator wouldn't run in eco mode, it needed to be at full RPM to carry 46A.
-The Iota IQ4 Charge controller has a float mode that holds the battery at 13.5V for 15 days without charging. Then it will switch to bulk mode, charge it back up and return to float mode. I think the reason it wouldn't charge at full output was because it was stuck in float mode. Unplugging the controller reset it. I need to do some reading and see if anyone else has noticed this. Other than that, I like the charge profile of the Iota.
-45A is definitely the largest charger I would run on a 1000watt generator. Its also about the largest charger I can use with my battery. 180 amp-hrs X 0.3C= 54A is the maximum recommended charge rate.
-It's really cool that I can replace 90 amp-hrs of capacity by running the generator two hours. I would have needed a full day to charge lead acid batteries back from that level.
-I use Victron Venus software running on a Raspberry Pi to track the battery voltage and current. I'd never know what was going on without it.
-I haven't had to run my generator while camping for a couple of years now, the PV array usually takes care of what we use. I like to have a backup power source since our fridge is electric.
Bruce