Other than this question, this schematic is a definate keeper.
Norm
powderburn wrote:Norm wrote:Question..., should there not be a GFCI somewhere on the AC input side?
Other than this question, this schematic is a definate keeper.![]()
Norm
The answer would be NO....
GFCI breakers and plugs have troubles running certain items.In bathrooms (with GFCI outlets),We get a lot of call backs because they trip when flourescent lights turn on.Not all but some do.
It is possable that the 2005 code(it hasnt been voted in yet) will start to require GFCI outlets on pedestals.
I think GFCI outlets SHOULD be used anywher you can,But there are a lot of places that they wouldnt be required on a TD.
The Galley should have GFCI in every location and if the light is 110v (in the galley), it should be fed off a GFCI also. A good rule of thumb is that,if you can reach the plug and touch the ground at the same time,it should be GFCI.
Hope that helps.
powderburn wrote:This is all I found about GFCI protection...
(C) Ground-Fault Circuit-Interrupter Protection. The internal wiring of a recreational vehicle having only one 15- or 20-ampere branch circuit as permitted in 551.42(A) and (B) shall have ground-fault circuit-interrupter protection for personnel. The ground-fault circuit interrupter shall be installed at the point where the power supply assembly terminates within the recreational vehicle. Where a separable cord set is not employed, the ground-fault circuit interrupter shall be permitted to be an integral part of the attachment plug of the power supply assembly. The ground-fault circuit interrupter shall provide protection also under the conditions of an open grounded circuit conductor, interchanged circuit conductors, or both.
powderburn wrote:If you read the code closely....It says
The internal wiring of a recreational vehicle having "only one" 15- or 20-ampere branch circuit as permitted in 551.42(A) and (B) shall have ground-fault circuit-interrupter protection for personnel.
I dont see where GFCI protection is required for multiple branch circuits or 30 ampre circuits.
Im with you though.A main braker that is GFCI is a very good idea.
quote
Now I didn't use a GFCI circuit breaker, I used GFCI receptacles, wiring from the line side of each one. I haven't had a problem with false trips when I've plugged into GFCI receptacles at the campground pedestal.
Also, GFCI receptacles seem to go bad all the time so I don't want to depend on just the campground GFCI.
There is a tester that can be plugged into a gfci protected recepticle that will test the GFCI to ensure its functionability.Maybe we could carry one of these in our TDs?.
Wiring from the "line" side of a GFCI will offer no protection so,in effect,it wouldnt cause false trips either,Wiring in this method would require you to instal a GFCI at every location.