2 wires 1 breaker ?

Anything electric, AC or DC

2 wires 1 breaker ?

Postby Rolly » Sat Sep 21, 2013 11:03 pm

I recently saw a breaker box with a circuit breaker with two 12ga wires tied to one breaker. There were a total of 6 plugs hooked to a 20 amp breaker. Is this safe? does this meet code? Would you do it in your trailer?

Rolly
User avatar
Rolly
Teardrop Advisor
 
Posts: 90
Images: 8
Joined: Thu Jan 28, 2010 2:41 am
Location: Salt Lake City, Ut

Re: 2 wires 1 breaker ?

Postby bdosborn » Sat Sep 21, 2013 11:39 pm

Having two wires under a single lug doesn't meet code. Having 6 receptacles on a 20A breaker does.

Bruce
2009 6.5'X11' TTT - Boxcar
All it takes is a speck of faith and a few kilowatts of sweat and grace.
Image
Boxcar Build
aVANger Build
User avatar
bdosborn
Donating Member
 
Posts: 5595
Images: 806
Joined: Wed May 05, 2004 11:10 pm
Location: CO, Littleton

Re: 2 wires 1 breaker ?

Postby H.A. » Mon Sep 23, 2013 4:35 pm

.
Last edited by H.A. on Sun Jan 17, 2016 2:15 pm, edited 1 time in total.
H.A.
The 300 Club
 
Posts: 461
Images: 0
Joined: Tue Nov 15, 2011 8:16 pm
Top

Re: 2 wires 1 breaker ?

Postby Dale M. » Tue Sep 24, 2013 8:05 am

IF its a trailer, what jurisdiction has authority over it if its on the move.... And do you call code inspection at each phase of build... Just saying..... Keep in mind its not a house which will be on same spot for 50 to 100 years, its a trailer... Use common sense during build and if it does not meet code it may not be a issue, just be sure its safe.....

Dale
Lives his life vicariously through his own self.

Any statement made by me are strictly my own opinion.
You are free to ignore anything I say if you do not agree.

Image
User avatar
Dale M.
2000 Club
2000 Club
 
Posts: 2693
Images: 18
Joined: Thu Jun 09, 2005 8:50 pm
Location: Just a tiny bit west of Yosemite National Park
Top

Re: 2 wires 1 breaker ?

Postby bdosborn » Tue Sep 24, 2013 8:36 pm

Just about every code has been enacted because someone got hurt or there was a fire. So you really should think twice before you poo-poo codes. Think about the audience here - most people have never wired 120V before. Short cuts and bad practice are not the kind of techniques we should be posting.

Bruce
2009 6.5'X11' TTT - Boxcar
All it takes is a speck of faith and a few kilowatts of sweat and grace.
Image
Boxcar Build
aVANger Build
User avatar
bdosborn
Donating Member
 
Posts: 5595
Images: 806
Joined: Wed May 05, 2004 11:10 pm
Location: CO, Littleton
Top

Re: 2 wires 1 breaker ?

Postby Dale M. » Tue Sep 24, 2013 9:22 pm

I am not POO-POOing anything.... Tell me specifically what codes cover ac wiring in a travel trailer....

Dale
Lives his life vicariously through his own self.

Any statement made by me are strictly my own opinion.
You are free to ignore anything I say if you do not agree.

Image
User avatar
Dale M.
2000 Club
2000 Club
 
Posts: 2693
Images: 18
Joined: Thu Jun 09, 2005 8:50 pm
Location: Just a tiny bit west of Yosemite National Park
Top

Re: 2 wires 1 breaker ?

Postby bdosborn » Tue Sep 24, 2013 9:46 pm

NFPA 70 (NEC) Article 551 - Recreational Vehicles.

Links to various forum discussions on 551

551 references various sections of the rest of the NEC as well. Including wire ampacity, over current protection, etc.

Bruce
2009 6.5'X11' TTT - Boxcar
All it takes is a speck of faith and a few kilowatts of sweat and grace.
Image
Boxcar Build
aVANger Build
User avatar
bdosborn
Donating Member
 
Posts: 5595
Images: 806
Joined: Wed May 05, 2004 11:10 pm
Location: CO, Littleton
Top

Re: 2 wires 1 breaker ?

Postby cpinetree » Sun Oct 20, 2013 7:35 pm

Some circuit breakers are rated for 2 wires, Square D's QO series is such a breaker. There may be others.I believe both wires should be the same gauge (like 2 #12's)
If the breaker is not designed for 2 wires you could always use a wirenut to combine the 2 wires plus an additional wire to attach to the breaker. [crude ascii art of that (load1+2===wn-----breaker)]
It meets NEC code, assuming the breaker manufacturer allows it, or you use the wirenut 2 wires into 1 method.
I would have no problem putting 10 recpts on 1 breaker as long as the load pulled through all of them at the same time does not exceed the amperage rating of the wire and the correct breaker is used for that wire gauge.
cpinetree
Donating Member
 
Posts: 51
Images: 18
Joined: Tue Feb 14, 2012 7:29 pm
Location: N Ft Myers, FL
Top

Re: 2 wires 1 breaker ?

Postby cpinetree » Sun Oct 20, 2013 7:49 pm

H.A. wrote:Despite meeting code, Its commonly discouraged as makes a messier installation and (in round-about theory anyway) makes the panel serve as a splice enclosure, what is not allowed in some jurisdiction.

Not allowed in some jurisdictions?? I think the practice of having local amendments override the code has been abandoned, and it would be an easy argument to win if the inspector said otherwise.
Using a panel as a junction box is not expressly disallowed by the NEC so therefore is code compliant (NEC is a permissive document. if it doesn't say you can't, you can.).
Panels are often used as junction boxes, especially when old fuse boxes that are in non code compliant locations (think closets, bathrooms, etc) are upgraded to circuit breakers.
cpinetree
Donating Member
 
Posts: 51
Images: 18
Joined: Tue Feb 14, 2012 7:29 pm
Location: N Ft Myers, FL
Top

Re: 2 wires 1 breaker ?

Postby bdosborn » Sun Oct 20, 2013 9:39 pm

cpinetree wrote:Not allowed in some jurisdictions?? I think the practice of having local amendments override the code has been abandoned, and it would be an easy argument to win if the inspector said otherwise.


Baahaahahaahahaahaahahaa. That's funny, I'm gonna circulate that one around the office. Good luck with that and let us know how it goes if you ever actually meet an electrical inspector.

Bruce
2009 6.5'X11' TTT - Boxcar
All it takes is a speck of faith and a few kilowatts of sweat and grace.
Image
Boxcar Build
aVANger Build
User avatar
bdosborn
Donating Member
 
Posts: 5595
Images: 806
Joined: Wed May 05, 2004 11:10 pm
Location: CO, Littleton
Top

Re: 2 wires 1 breaker ?

Postby bdosborn » Sun Oct 20, 2013 9:47 pm

cpinetree wrote:Some circuit breakers are rated for 2 wires, Square D's QO series is such a breaker. There may be others.I believe both wires should be the same gauge (like 2 #12's)


But there are a lot more breakers that aren't rated for two wires. Again, think about our audience, most people are doing 120V wiring for the first time. Lets keep it simple and recommend good practice - one wire to a breaker. Why make it complicated when a mistake could cost you your trailer?

Bruce
2009 6.5'X11' TTT - Boxcar
All it takes is a speck of faith and a few kilowatts of sweat and grace.
Image
Boxcar Build
aVANger Build
User avatar
bdosborn
Donating Member
 
Posts: 5595
Images: 806
Joined: Wed May 05, 2004 11:10 pm
Location: CO, Littleton
Top

Re: 2 wires 1 breaker ?

Postby cpinetree » Mon Oct 21, 2013 7:20 am

bdosborn wrote:
cpinetree wrote:Not allowed in some jurisdictions?? I think the practice of having local amendments override the code has been abandoned, and it would be an easy argument to win if the inspector said otherwise.


Baahaahahaahahaahaahahaa. That's funny, I'm gonna circulate that one around the office. Good luck with that and let us know how it goes if you ever actually meet an electrical inspector.

Bruce


We have the cell numbers to all the inspectors we deal with, as well as they have regular office hours.
We also try and meet the inspector on the job when we call in the inspection, that way if there are any questions / issues they can be corrected immediately.
cpinetree
Donating Member
 
Posts: 51
Images: 18
Joined: Tue Feb 14, 2012 7:29 pm
Location: N Ft Myers, FL
Top

Re: 2 wires 1 breaker ?

Postby cpinetree » Mon Oct 21, 2013 7:21 am

bdosborn wrote:
cpinetree wrote:Some circuit breakers are rated for 2 wires, Square D's QO series is such a breaker. There may be others.I believe both wires should be the same gauge (like 2 #12's)


But there are a lot more breakers that aren't rated for two wires. Again, think about our audience, most people are doing 120V wiring for the first time. Lets keep it simple and recommend good practice - one wire to a breaker. Why make it complicated when a mistake could cost you your trailer?

Bruce

Agreed, KISS method, one wire per breaker is the best practice for simplicity.
cpinetree
Donating Member
 
Posts: 51
Images: 18
Joined: Tue Feb 14, 2012 7:29 pm
Location: N Ft Myers, FL
Top