I've drawn this after reading dozens of posts and articles but there is a chance I have confused something, so feedback is appreciated.

Sent from my SM-G935V using Tapatalk
Viper_Twig wrote:
How should I calculate fuse size there?
Good explanation thanks. With 4awg for the batteries I'm thinking 150amp block fuse at the battery. Every other DC circuit will have an appropriate blade fuse at the PD4045 DC panel. I will add an inline fuse at the MPPT controller as well.MtnDon wrote:Viper_Twig wrote:
How should I calculate fuse size there?
The purpose of a fuse is to protect the wire against overheating, short circuit damage. So #1 would be to size the master fuse according to the battery cable and then size the fuses in the fuse block according to the size of the downstream wires. OR the master fuse could be smaller than what is called for wire protection, but at least as big as all the other circuit fuses combined. Neither would be wrong.
I will add an inline fuse at the MPPT controller as well.
Thanks. You are not wrong. The PD4045 is not an inverter. It is only a converter and AC/DC distribution panel. I may add a small inverter for light duty AC appliances while I am off grid. I plan on Boondocking without a generator 90% of the time so I need to keep my consumption within my solar/battery capacity.bc toys wrote:are you going to put a inverter in or just run DC power I may be wrong but I don't think the fuse box you show is a inverter I believe it will charge the battery but not convert DC to AC if I'm wrong let me know I am starting my solar this week had it sense June but just been to busy to install it By the way you are doing great work on your trailer