OverTheTopCargoTrailer wrote:Hi Bruce
thanks for advive ....since NEC is not checking my work![]()
why not use 10 amp dc breakers vs. 15 on each string - they would trip sooner ?
right now I have all 4 panels 210 x 4 @ 100 volts on a single 15 amp dc breaker
the midnight solar breakers are only $12 - cheap
The circuit breaker is there to protect the wire, not the panel. A #12 will is rated for 20 amps and will carry 20 amps forever, hence the 20 amp breaker. Remember that there will be times when the current may be higher than the panel rated output so you need to size everything higher than Imp of the panel. Also, molded case circuit breakers will trip at a lower current levels than the rated value when they're clustered together in a breaker box. They have a bimetallic strip in them that trips the breaker when it gets to a certain temperature, which depends on the load that's running through it. The breaker runs hotter when its bunched together with other breakers in a closed box. 80% is the typical rating the manufacturer recommends loading them to when they're not in free air.
Right now I have a 63 amp dc breaker from charge controller to the the Battery - I'm looking for a 80 but its harder to find ...
I purchased a Blue sea 80 amp breaker ( $59 - ouch ) that is easy to open & reset - that is my plan "B"
http://bluesea.com/category/3/10/productline/overview/433
Here's a link to a relabeled Bussmann circuit breaker which, BTW the Blue Sea is as well. You don't want to use an 80 amp breaker as you'll trip at full output. I would go with a 100A breaker.
100A Circuit Breaker
My out back wire is # 2 or 4 AWG and is only 2 ft long to the main bus bar... from there it is # 1 AWG - 4 ft more to the batteries.
# 2 marine stranded wire at 90 deg rating can pull 130 amps over 13 ft distance.
You really should have a #2 wire if you're going to use a 100A circuit breaker
I now have a 150 amp fuse at the batteries - since I blew the 75 testing the ac![]()
the MC4 wires are all # 10 and my runs are all supper short under 3- 6 ft each ...( the LG panels leads now actually have # 12 wire )
I was surprised to see 670 watts from my 4 x 210 panels , laying flat at 1:30 pm last week, max NOCT is 149 watts per panel = 596 watts normal max
when its FREEZING cold then the output goes up on the panels.
Psssssssst ....no wire on my trailer is el chepo .....they are all oversized & under fused
after all if it would burn down - I'll need to start over - its not like I can buy a new model OTTCT
down the street.
thanks again
![]()
![]()
P.S. so opening the panel breakers under load would not be a problem ?
as its written never disconnect MC4 panel connectors under load
Circuit breakers are typically rated for a limited number of operations under load. Check the specs of whatever you get.
OverTheTopCargoTrailer wrote:ok so now I get why using 15 amp on the panels vs 10 amp breaker.....for the panels
I'm still a little foggy on why the Flexmax 80 - ( rated at max 80 amp output) should have a 100 amp breaker ??
I would think if I pull more then 80 amps for a short time - its more likely for the charge controller to get fried ?
so would it not be be safer for the equipment with a 80 amp vs a 100 amp ?
or we could split the difference and go for 90 amps![]()
OverTheTopCargoTrailer wrote:Bruce
Are you on vacation![]()