norcal2 wrote:For noise reduction you can build a sound box that you can set the gen in or on top or around that can can take apart break down and store..they are not to hard to put together if noise is your concern and soundmat is pretty cheap..just a thought.ive seen a lot of them around noise concern areas.
Glenlivet wrote:I have the very inverter generator and a 5200 BTU window shaker, the specs of which I don't know. In steady cooling operation the A/C makes the generator operate in econo in the second step, but the initial startup surge is large enough that when the generator is in econ and cold and the A/C has not been run that day, the startup surge will most often stall the generator. However, once the generator is warmed up and the A/C has operated for 10 minutes then the A/C's cycling between fan only and fan with compressor barely makes the generator change cadence. If you make sure it's revved up on first startup (or is thoroughly warmed up) then if fellow campers don't mind the Champion inverter generator in its lower steps then they oughtn't mind it with that A/C running.
http://youtu.be/GTYvY162eyc
OverTheTopCargoTrailer wrote:As a mater of fact it did not start with my Magium 1000 PSW - rated 1700 max![]()
Don't really know why not ?
Or a compressor start capacitor and PTCR.khigh wrote:...
, with the takeaway "You need a really big inverter, a lot of batteries, and huge cable".
The current drawn by an induction motor is a function of the rotor speed. The applied voltage creates a rotating magnetic field. When the rotor is rotating at the same speed as this magnetic field, the input current is minimum.
When the rotor is stopped, the input current is a maximum. This is because the turning rotor produces a back EMF that reduces the input current. If the rotor is not turning, there is no back EMF, and the input current is the highest. This is refered to as the "locked rotor current" because it is the same current that would be drawn if the rotor were locked in place so it can't turn.
When a motor is first started, the rotor is stopped, so it draws the locked rotor current. The motor quickly starts turning, and the rotor current decreases. The current keeps droping until the rotor gets up to full speed. At that point the current is at minimum. (Full speed is slightly less than the speed of the rotating magnetic field, and depends on how much torque the motor must produce to turn the load).
http://forums.mikeholt.com/showthread.p ... post560036
warnmar10 wrote:Or a compressor start capacitor and PTCR.
My only experience is with my EU2000i and either a 5,000 or 8,000 btu window a/c. The Honda runs either of them effortlessly. If you're using a modern a/c unit with electronic control, the control won't allow it to short cycle. That is, once the thermistor is satisfied and the compressor shuts off, the control won't allow the compressor to attempt a restart for several minutes. This allows time for the low side and high side pressures to approach equilibrium such that the compressor isn't trying to start against head pressure.khigh wrote:That's true, too.
That's a part of my initial questioning on this unit with the "low power starting" to see if it had a hard start capacitor built in, or if it could be added, added to, replaced, beefed up, etc.
I have a feeling it's probably a little bitty one.
I'm looking forward to getting the unit and hopefully not tearing it up before I use it.