What is the RIGHT size of copper tubing for LPG?

The reason for this post is that I want to "design for purpose" my build propane system. I feel that running a 1/2" black iron pipe maybe a little bit too heavy and also could be more expensive that cooper tubing that I understand is OK to use for travel trailers, but what size is right?
Since I could not quite find such information on this board here, i.e. what diameter of tubing has to be used in the propane trailer system, I thought I'd start a thread to specifically discuss minimal required tubing size. I have to mention, that I am doing that at my own risk, I have no certifications in this field, so use it at your own risk and discretion.
If you find any errors in my discussion below, I'd appreciate if you please let me and everybody know.
Now, I thought that the tubing size would be driven by a total capacity of appliances I have in BTU, so let's start to summit it up:
1. Hydro Flame BRC-10A Furnace - requires input of up to 10,000BTU. I will assume 12,000btu, in case I will change it to forced air atwood compact furnace in the future.
2. Two Burner cooktop, Flame King - 7,200+5,200=12400BTU
3. Dometic RM211 Fridge (http://www.nationalserroscotty.org/resources/DometicRM211.pdf). I could not readily find online what is required BTU input for this unit, so I am going to safely assume 5000BTU, I am sure the real number is lower than that, just by seeing how small amount of heat is produced by similar units in real circumstances.
Next, since we all usually "overbuild" here, I will assume that all appliances may run at a full capacity, because it can theoretically happen:
12,000+12,400+5,000=29400BTU
Then with 29400BTU total requirement in mind, I've searched and found this table online (http://inspectapedia.com/plumbing/LP_Gas_Line_Sizing_LPGE_Co.pdf).
That table shows what is the maximum BTU capacity for every particular tubing size is required with 11"WC LPG pressure with 1/2" pressure drop. I should probably assume that such 1/2" pressure drop would be OK for most appliances and also the fact that pressure regulator can be adjusted slightly to increase this pressure at regulator output.
One more parameter is at play here, which is the length of tubing from my LPG bottle regulator to the appliances. I estimate my length will be at maximum of 15 feet.
So, as per first page, first table, first row - 3/8" tubing of 20 feet length will work for maximum of 34,000BTU.
Conclusion: I can run 3/8" tubing and use all three appliances at the same time.
Again let me know if I can be missing anything.
Thanks,
Oleg
Since I could not quite find such information on this board here, i.e. what diameter of tubing has to be used in the propane trailer system, I thought I'd start a thread to specifically discuss minimal required tubing size. I have to mention, that I am doing that at my own risk, I have no certifications in this field, so use it at your own risk and discretion.
If you find any errors in my discussion below, I'd appreciate if you please let me and everybody know.
Now, I thought that the tubing size would be driven by a total capacity of appliances I have in BTU, so let's start to summit it up:
1. Hydro Flame BRC-10A Furnace - requires input of up to 10,000BTU. I will assume 12,000btu, in case I will change it to forced air atwood compact furnace in the future.
2. Two Burner cooktop, Flame King - 7,200+5,200=12400BTU
3. Dometic RM211 Fridge (http://www.nationalserroscotty.org/resources/DometicRM211.pdf). I could not readily find online what is required BTU input for this unit, so I am going to safely assume 5000BTU, I am sure the real number is lower than that, just by seeing how small amount of heat is produced by similar units in real circumstances.
Next, since we all usually "overbuild" here, I will assume that all appliances may run at a full capacity, because it can theoretically happen:
12,000+12,400+5,000=29400BTU
Then with 29400BTU total requirement in mind, I've searched and found this table online (http://inspectapedia.com/plumbing/LP_Gas_Line_Sizing_LPGE_Co.pdf).
That table shows what is the maximum BTU capacity for every particular tubing size is required with 11"WC LPG pressure with 1/2" pressure drop. I should probably assume that such 1/2" pressure drop would be OK for most appliances and also the fact that pressure regulator can be adjusted slightly to increase this pressure at regulator output.
One more parameter is at play here, which is the length of tubing from my LPG bottle regulator to the appliances. I estimate my length will be at maximum of 15 feet.
So, as per first page, first table, first row - 3/8" tubing of 20 feet length will work for maximum of 34,000BTU.
Conclusion: I can run 3/8" tubing and use all three appliances at the same time.
Again let me know if I can be missing anything.
Thanks,