Is it safe to bridge

Converting Cargo Trailers into TTTs

Is it safe to bridge

Postby casjoker » Fri Aug 12, 2016 7:04 pm

I did a search and found two threads about builds where people have done this, so i am assuming it's safe but wanted to double check. Putting in a 30amp 2 pole breaker with a 30amp rv cord in a 7x14 cargo trailer. RV cord only has 3 wires(neutral, hot, ground), breaker box has 4 post, (2 hots, neutral bar and ground bar). Is it safe to run the one hot wire into one side and make a bridge wire to get power to the other side? I have two 15 amp breakers. One for dedicated AC unit 1200btu/12amp and the other will run two lights and a couple of outlets for generic use. I will use regular 110 house plugs, 30 amp campground plugs and also a 3400watt generator for power. No DC current at this time. Going for simplicity and with the the generator didn't see the need for DV.
casjoker
Teardrop Inspector
 
Posts: 2
Joined: Thu Aug 11, 2016 4:51 pm

Re: Is it safe to bridge

Postby flboy » Fri Aug 12, 2016 7:11 pm

Yes. The two hot bars are in the case of 2 phase power. You can run 120VAC off one phase and a neutral or 240VAC off the two phases. I have put the jumper in my breaker box. Just make sure the jumper is at least as a heavy gage as the input wires.


Sent from my SM-N900P using Tapatalk
Don (Flboy)

YouTube Video of Finished 6x12 Trailer:
https://youtu.be/6_-8cVdWUIA
YouTube Video of 7*18 with 2ft V-nose Trailer:
https://youtu.be/MUcMM86LA2g
User avatar
flboy
Gold Donating Member
 
Posts: 4265
Images: 378
Joined: Tue May 15, 2012 6:13 pm

Re: Is it safe to bridge

Postby casjoker » Fri Aug 12, 2016 8:22 pm

Yes, I used the same 10ga wire left over from splicing the incoming rv plug. Thanks!