madprinter wrote:I'll try pluging into anoughter GFI today and see if it works. And also check for a loose connection to my frame grounding.
If I had a reversed neautral at an outlet would it still trip with all the breakers off? Thanks for all of your help.
If it is tripping with all the breakers off, you either have something wired in before the breakers, you have a sneak circuit (or short) somewhere, or you have a bad GFI. Even though a GFI is not an overcurrent device it does sense current in order to determine that there is an imbalance. Somehow it is sensing more current on one hot/neutral leg than the other (the ground conductor is not used in the GFI's trip circuit). In a properly wired GFI the neutral and ground current would sum to equal the current in the hot conductor, if the ground current exceeds a very low threshold, the the neutral current will have dropped below trip level and the GFI will trip.
Theoretically, if all the breakers are off, the GFI would see nothing, it would be as if nothing was plugged in. There has to be something causing a current flow in order for the GFI to operate. However I once had a GFI outlet on the outside of a house that tripped every time it rained, with nothing plugged into it, there was nothing hardwired downstream of the GFI, moisture inside the GFI itself had to be causing the trip. I first put a new "weather proof" cover on it, but did not solve the problem until I replaced the GFI itself.
In your case I would check everything between the GFI and the breaker box on the trailer. Including wire, plugs, receptacles, the inlet, etc.