DMcCam wrote:
This is my running lights diagram.
Unless you're over 80" in width you don't need the three running lights in the center (just FYI). I'd rather have a third brake light there just to get people to quit staring at the teardrop and pay attention to the lights.

14-gauge is more than sufficient, most pre-made harness kits for boat and utility trailers are 16-gauge. I wouldn't dissuade you from using the larger wire, just letting you know it's not required.

Interior light plan.
If all that lighting is LED you don't need to use 14-gauge (though again it won't hurt). It's just a balance between space (for the wiring), cost, and weight.

For the 12V plugs and Fantastic Fan plan I'm thinking of separate runs of 12 gauge for safety sake or is this overkill?
From an electrical load standpoint...unless you're going to use multiple sockets at one time you don't need separate runs. But here's the thing...you always want to make sure any one run of wire has protection from overload (either a fuse or circuit breaker).
Each fuse or circuit breaker (cb) further up the line from the load needs to handle the full line of all loads that pass through it. That means you might have 4 branch circuits each with 10 amp fuses but if they feed to a main supply then that supply line needs a fuse to protect but will also handle the load of all the branch circuits. Confused yet?
Here's an example: let's say you determine that the max load on the whole electrical system in the camper (not including running lights since they really come from the tow vehicle) will be 45 amps. So what you need is (say) a 50 amp circuit breaker (or fuse) at the source...that's the positive terminal on the battery. Ideally it would be right on the battery (and Blue Sea Systems makes on terminal fuses), that way the main source wire connected to the battery is protected. Second best is to just get a fuse as close as you can to the positive terminal (within 7" is the standard on boats) and having nothing between the positive terminal and the fuse (or cb)...a master switch should be down line from the circuit protection.
The main source wire should run to a distribution box (typically a fuse block) and from there you'll run out individual branch circuits. Each individual branch circuit should have a load appropriate fuse (or cb) to protect that circuit.
The main thing to remember is that in every case the fuse or the circuit breaker is there to protect the wiring, not the load. Protection is about preventing a fire, not protecting a specific component (they should have their own fuses). With that in mind let's say you have a #10 wire that will easily support a higher load and off that wire you "T" circuits off with #16 wire. If you only have a fuse in the #10 run (let's say it's 25 amps) you're not protecting the wiring in the #16 runs. It would be quite easy for a load to heat the #16 wire up enough to melt the insulation and potentially start a fire and not blow the 25-amp fuse on the #10 wire. So it's important to fuse the #16 wire appropriately.
You always want the fuse for a particular circuit at the beginning of the circuit not just somewhere in the circuit.
So anyway, back to your sockets. You just need to think about whether what you'll plug into the sockets (and use all at once) will overload a 12-gauge wire. If not you can use one run to supply all the sockets. If so then you need to split them; maybe 2 on one circuit and 1 on the other, or maybe one per circuit as you've drawn. It just all depends on what the situation is.
This next part can get confusing...
Ever wonder why small 12-volt items often have a fuse inside their 12-volt socket? It's because they're being plugged into a circuit that has so much more capacity then they draw. Their load is so small relative to to capacity of the circuit that if something were to happen to them it would never blow the fuse on the circuit.
So, if you have a 12-volt socket fused for 25 amps and you have a 3-amp load almost nothing but a dead short is going to blow the fuse so the small load itself is fused to protect the circuit. Otherwise a small load could get so hot it could start a fire without blowing the 25-amp fuse (at least until it shorts out). Think it can't happen? I made my living for awhile investigating fires where that very thing did happen...often (mostly in outlets and small counter top appliances).
It's better to figure out what you want a particular 12-volt socket to support then fuse it for the item that will be plugged in rather than fuse the socket for its maximum possible load. That way the fuse will blow if something happens to the load, even if it's small.

This plan shows how the whole thing would connect in the tongue box.
I would swap places with the main fuse and the master switch.
Also as aggie79 (Tom) mentioned, it's not necessary to jumper the negative terminal on the battery to the chassis ground for any load that you have in the camper. However, since you've got a charging circuit from the tow vehicle you do need to have a complete circuit for that to work. If you're using the chassis for ground on the trailer lighting then the easiest way to get the complete circuit for the charging circuit is to jumper the battery's negative terminal to ground as well, just as you've drawn it.
This is supposed to be helpful not overbearing. If I put in all the qualifiers as I type it gets even longer.
I love your build!!!